Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: 480/208 Dual voltage transformers

User: Open Neutral, Location: Inside the Beltway

Asked on: Monday, January 3, 2011 at 1:18 am EST
Answered on: Monday, May 13, 2024 at 11:44 pm EDT

Question: We had planned to get a 480 3ph feed from PG&E for a large residence.At the meter, about 130 ft from the 22KV pole drop, we would add solar input, and go 800+ ft to the 112.5KVA house xfmr on pad we supply.This has various i$$ues, most related to how much PG&E want$ to do this. It would need a pad mount xfmr [not all bad] and new pole for the 22KV riser.It's possible we could save some money by taking their feed at 208/120, running it 130 ft, having the meter there, adding solar/etc; and then stepping it up to some common MV {say 4160}, going 800+ ft, and stepping down again.a) Is this even practical at those 208V power levels over 130 ft?b) We need both 480 and 208/120 at the house. We could have separate MV->480, MV->208/120 transformers, I guess, but do MV primary/dual secondary voltage units exist, outside of some custom build??

a) Practicality of 208V Over 130ft

Yes, it is practical to transmit 208V over 130ft at the power levels typical for a large residence. The voltage drop would be approximately 3.5V, which is within acceptable limits. The conductor size and circuit protection would need to be designed appropriately to minimize voltage drop and ensure safety.

b) MV Transformers with Primary/Dual Secondary Voltages

Yes, MV transformers exist with primary windings designed for a specific MV voltage and secondary windings providing both 480V and 208/120V output. These transformers are known as "primary/dual secondary" transformers or "multi-winding transformers." They are typically custom-designed and manufactured to meet specific requirements.

Recommended Approach

To save costs, you could consider the following approach: Take the PG&E feed at 208/120V. Install a 208/120V meter 130ft from the pole drop. Add solar input and other equipment at the metering point. Install a 208/120V-to-4160V step-up transformer. Run 4160V cables the remaining 800+ ft to the house. Install a 4160V-to-480V step-down transformer for the 480V loads.* Install a 4160V-to-208/120V step-down transformer for the 208/120V loads.This approach would reduce the high-voltage feeder cost and eliminate the need for a pad-mounted transformer and 22kV riser pole. It would also provide the flexibility to have both 480V and 208/120V power at the house. Flag for review

Previous Question Next Question