Question: On utility secondary services are C/T cabinets usually grounded? From the C/T cabinet drawing from the utility It indicated three phases and neutral from the utility xfmr. (not bonded N-G until it lands in the switchboard inside the building however the C/T is on the exterior of the bldg between the xfmr, and switchboard? Does this mean that the conductors from the xfmr to main switch are "ungrounded" since not N-G connection is made in the xfmr, and only 4-conductors are installed from the xfmr to the main switch?
Are C/T Cabinets Usually Grounded?
Yes, C/T (current transformer) cabinets on utility secondary services are typically grounded.
Circuit Diagram
The diagram you described from the utility indicates: Three phases (A, B, C) Neutral (N) No neutral-to-ground (N-G) bond in the transformerUngrounded Conductors
Based on the diagram, the conductors from the transformer to the main switch are indeed considered "ungrounded" because: There is no N-G bond in the transformer. Only four conductors (3 phases + neutral) are installed from the transformer to the main switch.
Neutral Grounding
The N-G bond is typically made inside the building's switchboard. This ensures that the electrical system is safely grounded and provides a path for fault currents to flow to the earth.
Reason for Ungrounded Conductors
Utility secondary services with ungrounded conductors are sometimes used in industrial or commercial facilities where specific equipment or processes require an isolated electrical system. For example: To prevent ground currents from interfering with sensitive electronic devices.* To provide a dedicated return path for fault currents, reducing the risk of stray currents in the facility.
Note: It's important to consult with the utility and follow local electrical codes and industry best practices when dealing with ungrounded systems. Flag for review