Topic: Pull boxes/manhole in underground conduits

User: LUIS FERNANDEZ, Location: Miami Fla.

Asked on: Monday, January 3, 2011 at 2:45 pm EST
Answered on: Monday, May 13, 2024 at 11:44 pm EDT

Question: Is there any code requirements for pullbox/manhole spacing?

Yes, code requirements exist for pullbox and manhole spacing. The National Electrical Code (NEC) provides these requirements in Article 300.15. It states that "Conductors shall be accessible for examination and servicing. The conductors shall be installed in conduits, raceways, or other enclosures as specified elsewhere in this Code."Additionally, the NEC provides specific requirements for the spacing of pull boxes and manholes in Sections 314.28 and 314.30

314.28 Pull Boxes.Pull boxes shall be spaced so that the distance between the centers of adjacent boxes, in feet, shall not exceed the distance calculated by the following equation (see Table 314.28):D = 70 x I x V x CWhere:D = Distance between pull boxes in feetI = Conductor current in amperesV = Voltage in voltsC = Conductor size adjustment factor

Table 314.28Conductor Size Adjustment Factor (C)Conductor Size (AWG) C14, 12 0.710, 8 1.16, 4 1.33, 2, 1, 1/0 1.52/0, 3/0, 4/0 1.7250, 300, 350, 400 2.0500, 600, 750 2.31000, 1250, 1500, 2000 2.8314.30 Manholes.Manholes (handholes are prohibited) shall be spaced so that the distance between adjacent manholes, in feet, shall not exceed that shown in Table 314.
30.

Table 314.30Cable Size and Manhole SpacingConductors per Cable Manhole Spacing, ft1-4 4005-12 30013-20 20021 or more 150These requirements aim to ensure that pullboxes and manholes are adequately spaced to facilitate the safe and convenient examination and servicing of conductors. Complying with these code requirements is crucial for maintaining the integrity and safety of electrical installations. Flag for review