Topic: 3 phase calculations for PDUs in data center

User: jotw, Location: Texas

Asked on: Monday, January 3, 2011 at 10:48 pm EST
Answered on: Monday, May 13, 2024 at 11:45 pm EDT

Question: Good evening. On an unrelated note, I just started a remodel today and took some pictures I think you all will get a kick out of. I'll post them when I get a chance.Alright. I know you all hate to just give answers and would rather give Articles. Unfortunately, I don't find anything relative to this particular installation. And, I think my math is way off. At least I hope it is. I am new to 3 phase calcs.The installation is as follows:2 - 40kw PDUs (480V input protected by 80A breaker)1 - Fire suppression system (120V w/ 20A breaker)1 - ten ton mini split AC system (don't have elec. requirements yet)The data center is approx. 200' from the service.I need help with sizing the disconnect and feeders. Any help is greatly appreciated.

Disconnect Switch Sizing

The disconnect switch must be rated for the maximum current that can flow through it. The maximum current is the sum of the currents for all the loads:

Maximum current = (40 kW + 40 kW) / 480 V + 20 A = 160 A
Therefore, the disconnect switch must be rated for at least 160 A.

Feeder Sizing

The feeder must be sized to carry the maximum current plus a safety factor. The safety factor is typically 25%, so:
Feeder current = Maximum current  1.25 = 160 A  1.25 = 200 A
The feeder must be sized to carry 200 A.

Conduit Sizing

The conduit must be sized to fit the feeder cables plus any other cables that may need to be run in the conduit. The exact conduit size will depend on the number and size of the cables, but a good starting point is to use a 2-inch conduit.

Note:

The calculations above are based on the assumption that the mini split AC system will require 20 A at 120 V. If the actual electrical requirements for the mini split AC system are different, the calculations will need to be adjusted accordingly. It is always best to consult with a qualified electrician to ensure that the installation is properly sized and installed. Flag for review