Question: Good evening. On an unrelated note, I just started a remodel today and took some pictures I think you all will get a kick out of. I'll post them when I get a chance.Alright. I know you all hate to just give answers and would rather give Articles. Unfortunately, I don't find anything relative to this particular installation. And, I think my math is way off. At least I hope it is. I am new to 3 phase calcs.The installation is as follows:2 - 40kw PDUs (480V input protected by 80A breaker)1 - Fire suppression system (120V w/ 20A breaker)1 - ten ton mini split AC system (don't have elec. requirements yet)The data center is approx. 200' from the service.I need help with sizing the disconnect and feeders. Any help is greatly appreciated.
Disconnect Switch Sizing
The disconnect switch must be rated for the maximum current that can flow through it. The maximum current is the sum of the currents for all the loads:
Maximum current = (40 kW + 40 kW) / 480 V + 20 A = 160 ATherefore, the disconnect switch must be rated for at least 160 A.Feeder current = Maximum current 1.25 = 160 A 1.25 = 200 AThe feeder must be sized to carry 200 A.