Topic: Lighting Breaker Tripping

User: chrisrappl, Location: Raleigh

Asked on: Tuesday, January 4, 2011 at 6:25 am EST
Answered on: Monday, May 13, 2024 at 11:46 pm EDT

Question: I could use some help troubleshooting an intermittently tripping lighting feeder breaker.The service is 277/480 3 phase/ 4 wire ? 2500 amp main breaker with ground fault protection (GFP).Downstream are two switchboard sections containing GE TJL breakers. The lighting breaker (Lighting panels on the 1st and 2nd floor) and the breakers for the 1st and 2nd Fl power panels are equipped with GFP; the breakers for the UPS and EHVAC are not equipped with GFP.Since the main has GFP, I do not think that the code requires GFP on the lighting and power feeder breakers; however the original engineer (20+ years ago) must have had his reasons.The lighting feeder breaker (TJL4V2603) with micro versa trip (T4VTG) is a 300a breaker that normally is loaded to about 10% (A-33.9a, B-27.1a, C-19.4a). It had tripped previously (maybe once every few years). In the past month or so it has tripped almost every week. (No changes or additions that we are aware of ? the lighting panels also contain some single phase 277v circuits for VAVs - a few years ago an underground backflow preventer was replaced with an above ground unit that may have a heater for freeze protection. I need to investigate since the pole lighting is the only power in the vicinity.) I don?t think that these GE breakers are known to nuisance trip when lightly loaded and unbalanced, but it?s not a good situation.12/2/10 7:40pm12/10/10 7:39pm12/16/10 6:30pm12/21/10 7:43pm12/24/10 6:04pmSince all the tripping has occurred after dark I looked into the five exterior lighting circuits (photo cell controlled through contactors). We made sure that all the pole lights, bollards and exterior building lights were in good operable condition and then operated with the two pole light circuits off (breaker tripped), with the two bollard circuits off (breaker tripped) and with the building exterior lighting circuit off ( breaker tripped). After the 3rd or 4th trip, the building technician noted that each time, as he was heading over to the building to reset the breaker, he was passing the night cleaning lady as she was leaving the building. We have spoken to the cleaning lady and are in the process of reviewing the security cameras for clues. (Maybe those are her nights for cleaning the breakers?On the 21st, the lighting breaker and the breaker directly beneath it (power ? 2nd fl.) were tripped. The 2nd floor power feeder is a 3 wire feeder with no neutral however; there is a pair of control wires coming to the breaker from an unused neutral CT. Interestingly the micro versa trip on the power breaker is a T4VTNG. I would assume that the ?N? designates neutral. As far as the 2nd floor power breaker being tripped, I suspect human error. The tech who responded did not know how to reset the lighting breaker and he may have accidentally pushed the trip button on the breaker below while trying to reset the lighting breaker, but? It may be a clue.The electrical room where the breakers are located also contains a large UPS. The original UPS had battery racks of large wet cells that overcharged a couple of years ago and more than half of the electrolyte boiled out into the atmosphere of the room. Acid swab tests on the walls and equipment were unremarkable. Mostly the water evaporated leaving a higher acid concentration in the cells, but? It may also be a clue. Solid state boards in the breakers could have been affected.I?m sure that I need to continue looking for a downstream ground fault; however, I think that I should schedule a shutdown and trace the CT control wires to each breaker, making sure that the lighting neutral CT is connected to the lighting breaker. I also need to know if the lighting breaker should have the T4VTNG micro versa trip unit. The T4VTG units do have two control terminals and each has a pair of wires coming up form their respective, unused neutral CTs, so they must be designed for neutral current, but why the difference of the ?N? in the designation? And why isn?t the one feeder with a neutral connected to the trip unit with an ?N??I wish I knew why the original engineer required GFP on the lighting and power panel feeders. I am almost tempted to replace the T4VTG trip unit with a T4VT unit with no GFP, or just replace the TJL breaker with a basic TJK frame breaker with no GFP. However, I would not want to take a chance that whatever is causing the lighting breaker to trip could cause the main breaker to trip since it also has ground fault protection.

Troubleshooting



1. Inspect Lighting Circuits

Check all exterior lighting circuits for loose connections, damaged insulation, or faulty fixtures. Verify proper operation of photo cell contactors and wiring.

2. Examine Breaker Trip Data

Note the time and date of each trip and any patterns (e.g., after dark). Inspect the breaker for any visible damage or signs of overheating.

3. Trace CT Control Wires

Verify that the lighting neutral CT is correctly connected to the lighting breaker. Check the CT connections for the 2nd floor power breaker to ensure they are not compromised.

4. Investigate Possible Clues

Interview the cleaning lady and review security footage for any suspicious activity near the electrical room. Consider the possibility of residual acids from the UPS battery incident affecting breaker components.

5. Check Micro Versa Trip Units

Determine the correct type of trip unit for the lighting breaker (T4VTG or T4VT). Inspect the trip unit for proper installation and operation.

6. GFP Evaluation

Determine if the lighting and power panel feeders still require GFP. Consider replacing the GFP trip units with non-GFP units or replacing the breakers with non-GFP models. However, this decision should be made carefully to avoid compromising safety.

Additional Considerations

Monitor the load on the lighting feeder to ensure it is not exceeding the breaker's capacity. Perform insulation resistance testing on the lighting circuits to identify any potential ground faults. Consider installing ground fault current interrupters (GFCIs) or arc fault circuit interrupters (AFCIs) at critical locations to provide additional protection.

Recommendations:


Based on the information provided, the following recommendations are suggested:
Continue investigating for downstream ground faults. Trace the CT control wires and verify correct connections. Determine the appropriate micro versa trip unit for the lighting breaker. Consider replacing the GFP trip units or breakers if the GFP requirement is not necessary. Monitor the lighting feeder load and perform insulation resistance testing. Flag for review