Topic: MV Wire on LV Circuits

User: ThomasSchlitt, Location: Evansville, Indiana

Asked on: Tuesday, January 4, 2011 at 9:03 am EST
Answered on: Monday, May 13, 2024 at 11:46 pm EDT

Question: Are there any regulations, rules of thumb, etc. against using 5kv or even 15kv single insulated copper conductors such as transformer jumper lead for 480V circuits in protected installations? I haven't been able to locate anything in the code that inhibits its use.NEC Table 310.60(C)(69) indicates an ampacity of 695A at 90deg C for a 5KV, 500MCM cable. On a 2000A circuit, one could install 3 conductors per phase instead of 6 if terminated effectively at 90 deg C and installed properly.

NEC Regulations NEC Table 310.15(C)(1) requires that conductors with voltage ratings less than the circuit voltage not be used. However, this rule does not explicitly specify single-insulated conductors. NEC Article 215.2(A)(1) requires that conductors for circuits above 1000 volts be installed in a manner to prevent contact with other conductors and grounded surfaces. NEC Article 300.19 prohibits the use of single-insulated conductors in raceways, cables, or other enclosures except as specifically permitted.

Interpretation

Based on these regulations, the use of 5kv or 15kv single-insulated copper conductors for 480V circuits is generally prohibited. The voltage rating of the conductor must be equal to or greater than the circuit voltage.

Exceptions

There are a few exceptions where single-insulated conductors can be used at voltages below their rated voltage, including:
NEC Article 300.35 permits the use of 600V single-insulated conductors in raceways, cables, or other enclosures where all conductors are fully insulated for the circuit voltage.* NEC Article 408.34 permits the use of 600V single-insulated conductors in switchboards and panelboards where the conductors are fully insulated for the circuit voltage.

Recommended Practice

Although not explicitly prohibited by the NEC, it is generally not recommended to use 5kv or 15kv single-insulated copper conductors for 480V circuits. This is because the insulation thickness on single-insulated conductors is typically thinner than on conductors rated for higher voltages, increasing the risk of electrical breakdown.In addition, the use of single-insulated conductors in raceways, cables, or other enclosures may violate NEC Article 300.19, which requires all conductors to be fully insulated for the circuit voltage.

Conclusion

While the NEC does not explicitly prohibit the use of 5kv or 15kv single-insulated copper conductors for 480V circuits, it is generally not recommended due to safety concerns. It is best practice to use conductors with a voltage rating equal to or greater than the circuit voltage for all applications. Flag for review

Previous Question Next Question