Topic: MV Wire on LV Circuits

User: ThomasSchlitt, Location: Evansville, Indiana

Asked on: Tuesday, January 4, 2011 at 9:08 am EST
Answered on: Monday, May 13, 2024 at 11:46 pm EDT

Question: Are there any regulations, rules of thumb, etc. against using 5kv or even 15kv single insulated copper conductors such as transformer jumper lead for 480V circuits in temporary protected installations? I haven't been able to locate anything in the code that inhibits its use.NEC Table 310.60(C)(69) indicates an ampacity of 695A at 90deg C for a 5KV, 500MCM cable. On a 2000A circuit, one could install 3 conductors per phase instead of 6 if terminated effectively at 90 deg C and installed properly.

NEC Requirements for Temporary Protected Installations

NEC Article 305 covers the requirements for temporary protected installations. While this article does not explicitly prohibit the use of 5kV or 15kV conductors for 480V circuits, it does have important requirements that must be met

NEC 305.4(A)(1)

states that all conductors used in temporary protected installations must be suitable for the conditions of use. This includes being rated for the voltage, ampacity, and temperature rise.

NEC 305.4(A)(3) requires that temporary wiring must be protected from physical damage and insulated for the voltage involved. This means that 5kV or 15kV conductors must be adequately insulated for use on a 480V circuit.

UL Regulations

While the NEC does not directly prohibit the use of higher voltage conductors for lower voltage circuits, Underwriters Laboratories (UL) has regulations that may apply.

UL Standard 83 for Thermoplastic-Insulated Wires and Cables specifies voltage ratings for different types of insulation. For single-insulated copper conductors, UL 83 typically assigns the following voltage ratings: 600V - 1000V: Rated for voltages up to 1000V 2000V - 5000V: Rated for voltages up to 5000VExceptions

There are some exceptions to the general rule of using conductors rated for the voltage involved. NEC 305.4(A)(4) allows the use of higher voltage conductors in certain situations, such as: When the higher voltage conductors are used as feeders or branch circuits in a subpanel. When the higher voltage conductors are used within a listed assembly or piece of equipment.

Conclusion

While the NEC does not explicitly prohibit the use of 5kV or 15kV conductors for 480V circuits in temporary protected installations, it is important to carefully consider the following: The conductors must be suitable for the conditions of use, including voltage rating, ampacity, and temperature rise. The conductors must be adequately insulated for the voltage involved. UL regulations may impose additional voltage rating requirements. Exceptions to the general rule of using conductors rated for the voltage involved may apply.It is highly recommended to consult with a qualified electrician or electrical inspector to ensure that the use of higher voltage conductors is appropriate and compliant with all applicable codes and standards. Flag for review