Question: Are there any regulations, rules of thumb, etc. against using 5kv or even 15kv single insulated copper conductors such as transformer jumper lead for 480V circuits in temporary protected installations? I haven't been able to locate anything in the code that inhibits its use.NEC Table 310.60(C)(69) indicates an ampacity of 695A at 90deg C for a 5KV, 500MCM cable. On a 2000A circuit, one could install 3 conductors per phase instead of 6 if terminated effectively at 90 deg C and installed properly.

Code Requirements

The National Electrical Code (NEC) does not specifically prohibit the use of 5kV or 15kV single insulated copper conductors for 480V circuits in temporary protected installations. However, several code requirements must be met when using higher voltage conductors: Article 110.3(B) requires electrical installations to be installed and maintained to prevent recognized hazards. Article 300.1(A) requires wiring to be suitable for the conditions of use. Article 310.10(A) requires the ampacity of conductors to be sufficient for the maximum load. Article 310.10(B) requires conductors to be protected against overcurrent. Article 310.4 requires single insulated conductors to be installed in electrical metallic tubing (EMT), conduit, or other means listed for the purpose.

Other Considerations

In addition to the code requirements, there are several other factors to consider when using higher voltage conductors:
Arc Flash Hazard

5kV and 15kV conductors can create a significant arc flash hazard if faulted. Proper personal protective equipment (PPE) and arc flash analysis should be used to mitigate this hazard.

Insulation Thickness

The insulation thickness on 5kV and 15kV conductors is typically thinner than on lower voltage conductors. Care must be taken to ensure that the insulation is not damaged during installation or use.


Termination

Proper termination of higher voltage conductors is critical to prevent flashovers. Qualified personnel should perform all terminations according to the manufacturer's instructions.

Recommendation


While it may be possible to use 5kV or 15kV single insulated copper conductors for 480V circuits in certain temporary protected installations, this practice is not recommended. The increased arc flash hazard, insulation thickness concerns, and termination difficulties make it more prudent to use conductors that are specifically listed for the intended application. Flag for review