Question: Wondering if you guys can help me out? Working on a well pump station project that has a 250 HP pump (310 FLA) being installed. The service to the building is 600 Amp @ 480V,3Ph. The pump has an Allen Bradly Magnetic Starter. I'm not sure what size breaker I should utilize?Thanks
Estimated Full Load Current (FLC)
FLA = 310 amps
National Electrical Code (NEC) Requirements
For induction motors over 100 HP, the overcurrent protection (OCP) device should be rated at no more than 250% of FLC.
Overcurrent Protection (OCP) Device Sizing
OCP Rating = FLC x 250% OCP Rating = 310 amps x 2.5
OCP Rating = 775 ampsRecommended Breaker Size
Based on the calculated OCP rating of 775 amps, the recommended breaker size is
800 amps. This will provide sufficient overcurrent protection while allowing for the starting surge current of the motor.
NEC Exception
If the motor has inherent protection against sustained overload currents, such as a thermal overload relay, the OCP device can be rated at 175% of FLC (as opposed to 250%). In this case, the OCP rating would be 310 amps x 1.75 = 542.5 amps, which would require a
600 amp breaker. However, since this is below the service size, the recommended 800 amp breaker is still more appropriate.
Additional Considerations: Verify the voltage and amperage rating of the Allen Bradley Magnetic Starter. Install a thermal overload relay to protect the motor from sustained overloads. Consult with the pump manufacturer and local authority having jurisdiction (AHJ) for specific requirements and approvals. Flag for review