Topic: Sizing Breaker for 250HP pump

User: Jimmy4645, Location: San Francisco Bay Area, CA, USA

Asked on: Tuesday, January 4, 2011 at 10:38 am EST
Answered on: Monday, May 13, 2024 at 11:47 pm EDT

Question: Wondering if you guys can help me out? Working on a well pump station project that has a 250 HP pump (310 FLA) being installed. The service to the building is 600 Amp @ 480V,3Ph. The pump has an Allen Bradly Magnetic Starter. I'm not sure what size breaker I should utilize?Thanks

Estimated Full Load Current (FLC)

FLA = 310 amps

National Electrical Code (NEC) Requirements

For induction motors over 100 HP, the overcurrent protection (OCP) device should be rated at no more than 250% of FLC.

Overcurrent Protection (OCP) Device Sizing

OCP Rating = FLC x 250% OCP Rating = 310 amps x 2.5

OCP Rating = 775 amps
Recommended Breaker Size

Based on the calculated OCP rating of 775 amps, the recommended breaker size is

800 amps
. This will provide sufficient overcurrent protection while allowing for the starting surge current of the motor.

NEC Exception

If the motor has inherent protection against sustained overload currents, such as a thermal overload relay, the OCP device can be rated at 175% of FLC (as opposed to 250%). In this case, the OCP rating would be 310 amps x 1.75 = 542.5 amps, which would require a

600 amp
breaker. However, since this is below the service size, the recommended 800 amp breaker is still more appropriate.

Additional Considerations:
Verify the voltage and amperage rating of the Allen Bradley Magnetic Starter. Install a thermal overload relay to protect the motor from sustained overloads. Consult with the pump manufacturer and local authority having jurisdiction (AHJ) for specific requirements and approvals. Flag for review