User: MeterBase, Location: Moore, OK
Asked on: Tuesday, January 4, 2011 at 11:51 am EST
Answered on: Monday, May 13, 2024 at 11:47 pm EDT
Question: 70E paragraph 110.9(B)(4) - "Employee's hands shall not be wet when plugging and unplugging flexible cords and cord-and-plug connected equipment if energized equipment is involved."I'm looking at some standard, 120 volt outdoor receptacles installed to charge small electric vehicles via common extension cords listed for outdoor use. These outdoor receptacles meet 406.(B) requirements. Based on the 70E requirement above, it would seem that energized charging cords cannot be handled bare handed during inclement weather. It is not realistic to assume that people will only charge their vehicles in sunny, dry weather. I'm recommending the installation of a weatherproof switch ahead of each receptacle so people can turn off the receptacle before handling the charging cord.Has anyone else addressed (or would address) this issue differently?
The requirement in 70E 110.9(B)(4) is intended to prevent electric shock hazards that can occur when wet hands come into contact with energized electrical equipment. This is particularly important for flexible cords and cord-and-plug connected equipment, as these are often used in portable applications where there is a greater risk of contact with moisture.In the case of outdoor receptacles used to charge electric vehicles, the risk of electric shock is further increased by the presence of water and other conductive materials that may be present on the ground. This is especially true during inclement weather, when the likelihood of wet hands is greater.While it is not realistic to assume that people will only charge their vehicles in sunny, dry weather, there are several steps that can be taken to mitigate the risk of electric shock, including: Installing a weatherproof switch ahead of each receptacle, as you have recommended. This will allow people to turn off the power to the receptacle before handling the charging cord. Using a ground fault circuit interrupter (GFCI) to protect the circuit. GFCIs are designed to trip and cut off power to the circuit if they detect a difference in current between the hot and neutral wires, which can occur when there is a fault to ground.* Educating users about the dangers of handling energized electrical equipment with wet hands, and providing them with instructions on how to safely charge their vehicles.By taking these steps, you can help to reduce the risk of electric shock hazards associated with outdoor receptacles used to charge electric vehicles. Flag for review