Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Multiple Earth Grounds

User: jcoghlan, Location: Massachusetts

Asked on: Tuesday, January 4, 2011 at 12:41 pm EST
Answered on: Monday, May 13, 2024 at 11:47 pm EDT

Question: I have a situation where the electrical service is coming into the Main Panel of a facility where the Neutral, Safety Ground, and Earth Ground are all bonded together. So far so good... However, there is a branch circuit feeding out from the main approximately 100 yards to an outbuilding. While the Neutral and Grounds are not bonded there, the power user has established a separate Earth Ground reference at the outbuilding where he has connected the Ground conductors from Surge Suppressors to the separate Earth Ground. The two Earth Grounds are not bonded together. I know that I have a potentially serious Ground Loop issue here. So, while it is obvious this is not a true single point Grounding configuration, My question is; Does this particular Earth Ground configuration violate NEC?

Yes, this Earth Ground configuration violates Article 250.4(A)(5) of the National Electrical Code (NEC), which states:"The grounding electrode system shall not be used as the sole equipment grounding return path."In this case, the separate Earth Ground reference at the outbuilding is creating a parallel ground path for the equipment grounding conductors. This can cause ground loops and, if fault current flows through this parallel path, it can result in hazardous voltages on equipment or other conductive surfaces.To resolve this issue, the two Earth Grounds must be bonded together at the Main Panel. This will ensure that all equipment grounding conductors are connected to the same ground reference and that there is no potential for ground loops. Flag for review

Previous Question Next Question