User: lquadros, Location: CA
Asked on: Tuesday, January 4, 2011 at 2:22 pm EST
Answered on: Monday, May 13, 2024 at 11:47 pm EDT
Question: There is a 20amp. 480V stick welder. It needs to be moved around in the plant as required. We will need at least 30m. long cable. The available wall recaptacles are 60amps. The welder has a 20amp. breaker. What would be the minimum size of cable required to connect this welder? Your replies are appriciated
Step 1: Calculate the Load Current
Load current (I) = Welder current (20 A)Step 2: Determine the Voltage Drop
Voltage drop (Vdrop) = I Length of cable (L) Resistance per unit length (R)Step 3: Calculate the Resistance per Unit Length
The resistance per unit length can be found using the following formula:R = Resistivity (ρ) / Area (A)For copper cables, the resistivity is approximately 1.68 10^-8 ohm-meters.
Step 4: Determine the Required Area
Rearranging the Resistance per Unit Length formula, we get:A = R L / ρStep 5: Choose the Cable Size
Based on the calculated area, you can choose the appropriate cable size from a wire table. The following steps provide a general guideline: For short distances (less than 50 feet), use a 6 AWG cable. For medium distances (50-100 feet), use a 4 AWG cable. For long distances (over 100 feet), use a 2 AWG cable.
In this case, with a load current of 20 A and a length of 30m (approximately 98 feet), a 6 AWG cable would likely be sufficient.Additional Considerations: The 60amp wall receptacles may not be sufficient to power the welder. It is recommended to have a 100amp receptacle installed. Ensure that the welder is grounded properly to prevent electrical shock. Use a strain relief device to protect the cable from damage when moving the welder. Flag for review