Question: I may seem ignorant. I have a 480/277 volt panel to feed a transformer. Can a 480v primary 3 phase transformer be fed from this panel, or should the tansformer say 480/277v primary? The secondary is 120/208vac 3 phaseThanksBill
You can use a 480V primary 3-phase transformer to feed from a 480/277V panel. The transformer's primary voltage rating should match the voltage of the power source, in this case, 480V. The transformer's secondary voltage rating should match the desired output voltage, in this case, 120/208VAC. Flag for review