User: augie47, Location: Tennessee
Asked on: Tuesday, January 4, 2011 at 6:51 pm EST
Answered on: Monday, May 13, 2024 at 11:49 pm EDT
Question: Taking into account that the NEC directly addresses voltage drop as a non-enforceable FPN, I've been asked for my opinion on a situation.Without given a specific load or specific wire size, if a job (industrial) calls for a circuit to feed 120v receptacles at various locations is there any "accepted standard" where a certain maximum voltage drop would be mandated ?Specifically a plant asked for a 20 amp circuit with convenience outlets at various locations and are now concerned that with a 12 amp load the voltage drop is excessive for items being plugged in.If the job consisted of ONE duplex as opposed to multiple outlets, would that make a difference ?My opinion is that, without specifying a load, the calculated load of 180va would be all that would be applicable to the E/C.
Accepted Standard for Voltage Drop
While the NEC does not enforce specific voltage drop limits, there are accepted industry standards that provide guidelines.According to the Institute of Electrical and Electronics Engineers (IEEE) Standard 141, the recommended maximum voltage drop for industrial power systems is 5% for circuits with loads of 100% or less, and 3% for circuits with loads of 100% to 200%.
Specific Situation
In the given situation: Multiple Outlets
For a circuit feeding multiple outlets, the IEEE standard would recommend a maximum voltage drop of 5% for a load of 180 VA (12 A at 120 V).
Single Outlet
For a circuit feeding a single duplex outlet, the IEEE standard would recommend a maximum voltage drop of 3% for a load of 180 VA.
Difference between Multiple and Single Outlets
The difference in voltage drop limits between multiple and single outlets is due to the fact that multiple outlets can be used simultaneously, creating a higher potential load.
Load Considerations
The calculated load of 180 VA is based on the assumption that all outlets will be used at their full capacity. However, in reality, it is unlikely that all outlets will be loaded to their maximum. Therefore, the actual voltage drop may be lower than the calculated value.
Conclusion
Based on the IEEE standard, the following voltage drop limits would be recommended for the given situation: Multiple outlets: Maximum 5% voltage drop for a load of 180 VA Single outlet: Maximum 3% voltage drop for a load of 180 VAIt is important to note that these are recommendations and not enforceable requirements. The final decision on acceptable voltage drop should be made in consultation with the plant and based on the specific application and equipment used. Flag for review