User: Trowbridge - Martin, Location: Chapel Hill, NC
Asked on: Wednesday, January 5, 2011 at 6:22 am EST
Answered on: Monday, May 13, 2024 at 11:49 pm EDT
Question: A prefab gas ventless fireplace is being installed with a battery operated starter. The metal gas pipe 2 ft long, from outside connects to/thru fireplace. Does gas pipe need to be bonded ? What is forums definition of "likely to become energized"?Thank you, Tom310.1 Gas pipe bonding. Each above-ground portion of a gas piping system that is likely to become energized shall be electrically continuous and bonded to an effective ground-fault current path. Gas piping shall be considered to be bonded where it is connected to appliances that are connected to the equipment grounding conductor of the circuit supplying that appliance.
Does gas pipe need to be bonded?
Yes, the gas pipe needs to be bonded if it is likely to become energized.
Definition of "likely to become energized"
The NEC does not provide a specific definition of "likely to become energized." However, the term is generally interpreted to mean that the gas pipe is connected to an appliance that is likely to become energized or is in close proximity to an appliance that is likely to become energized.In this case, the gas pipe is connected to a ventless fireplace that is being installed with a battery operated starter. The fireplace is likely to become energized when it is turned on, so the gas pipe must be bonded.
How to bond the gas pipe
The gas pipe can be bonded by connecting it to the equipment grounding conductor of the circuit supplying the fireplace. The equipment grounding conductor is typically a bare copper wire that is connected to the grounding terminal of the electrical panel.
Additional information
It is important to note that the NEC requires all gas piping to be electrically continuous. This means that all joints in the gas piping must be made with approved fittings that maintain electrical continuity. Flag for review