User: mark32, Location: Currently in NJ
Asked on: Wednesday, January 5, 2011 at 8:39 am EST
Answered on: Monday, May 13, 2024 at 11:49 pm EDT
Question: A fellow electrician, whom I just met, is redoing the service on his house because he is turning it into a two family so he wants to add a meter and a sub panel, of which would be located upstairs.His plans are as follows: 4/0 AL SE into metallic trough (3R) via a hub, nipple out of trough with metallic offset nipples, one goes to 100a meter, the other into a 200a meter, then LB out of each meter and run into basement where one feeds 200a main panel, the other feeds a 100a disconnect that in turn feeds sub upstairs. I asked him how he was going to bond the trough, he said the nipples coming up from the meters will accomplish that. I said I don't think so but didn't push the topic as I've never done such an install, the same goes for the tap for the 100a side. He was going to tap it with #2 AL but then went up to 2/0 AL. Inside he already has, I believe, #4 copper AC feeding the sub which now that I think of it could be an issue as AC's ampacity is to be found in the 60c column yes? So instead of the 100a disc use a 100a main breaker panel and feed the #4 copper with a 70a breaker? Excuse me for getting side tracked, so here is how I envision the service assembled with the parts he wishes to use: Tap or bolt (Which is preferred?) a distribution block to the trough and terminate the neutral to that, then use bonding bushings on the offset nipples on the trough side and bond that to the block, if he was using a metallic raceway leaving the meters (Which he's not) use bonding bushings on the connectors when they enter their respective panels/disconnects. Oh, and use #1 AL for the 100a tap. What do you think?
Bonding the TroughYour method
Tapping or bolting a distribution block to the trough and terminating the neutral to it Using bonding bushings on the offset nipples on the trough side and connecting them to the distribution blockThis method is correct and achieves the required bonding between the trough, the conduit nipples, and the distribution block.
His method
Assuming he uses metallic nipples coming up from the meters, he believes that these nipples will bond the trough.This method is incorrect. While the metallic nipples will bond the conduit and meter connections, they will not effectively bond the trough itself, which is the main purpose of bonding in this situation.
Tap for the 100A SideYour suggestion
Use a 100A main breaker panel and feed the #4 copper with a 70A breakerThis suggestion is correct. Since the AC ampacity of #4 copper is found in the 60°C column, a 70A breaker is the appropriate choice for the 200A service.
Additional ConsiderationsMetering Configuration
The proposed metering configuration (one 100A meter and one 200A meter) is typically used when the main and sub services have different billing arrangements. Ensure that the meters are configured correctly according to the intended use.
Using Metallic Raceways Leaving the Meters
If metallic raceways are used leaving the meters, bonding bushings should be installed on the connectors where they enter their respective panels/disconnects to provide a continuous bond from the trough to the panel/disconnect enclosures.
Overall, your proposed assembly method for the service with the provided parts is correct. Ensure that all materials and installations comply with applicable electrical codes and standards. Flag for review