Topic: Outdoor Heaters

User: Dustin Foelber, Location: NC & IN

Asked on: Wednesday, January 5, 2011 at 10:06 am EST
Answered on: Monday, May 13, 2024 at 11:50 pm EDT

Question: Good Morning GentlemenI have a Dual element 5000 Watt heater we are installing. This unit has a primitive controller that works with a Numbered dial but is basically just a time delay relay that cycle the single phase 240 feed on and off. THe controller has 2 dials one for each element. The wiring is about 20 feet from the load side of each element relay to the heater with the (2) independant 2500 watt elements. My question is I have 10 awg on a 30 amp breaker running to the controller which then pigtails to feed the line side of both dials. Am I permitted to run 12 from the load side of each dial to each element??Thanks

Yes, you are permitted to run 12 AWG wire from the load side of each dial to each element, provided that the following conditions are met: Current carrying capacity

12 AWG wire is rated for a maximum current of 25 amps. Since each element is rated at 2500 watts, the current draw at 240 volts is approximately 10.42 amps. Therefore, 12 AWG wire can safely handle the current.


Voltage drop

The voltage drop over the 20-foot wire run should be calculated to ensure that the voltage at the element is within acceptable limits. Using Ohm's law (V=IR), the voltage drop over 20 feet of 12 AWG wire carrying 10.42 amps is approximately 0.44 volts. This is a negligible amount and will not significantly affect the operation of the element.*

Overcurrent protection:
The 30 amp breaker at the load side of the controller provides adequate overcurrent protection for both elements.Therefore, it is permissible to use 12 AWG wire from the load side of each dial to each element, provided that the above conditions are met. Flag for review