User: Dustin Foelber, Location: Illinois
Asked on: Wednesday, January 5, 2011 at 10:07 am EST
Answered on: Monday, May 13, 2024 at 11:50 pm EDT
Question: Good Morning GentlemenI have a Dual element 5000 Watt heater we are installing. This unit has a primitive controller that works with a Numbered dial but is basically just a time delay relay that cycle the single phase 240 feed on and off. THe controller has 2 dials one for each element. The wiring is about 20 feet from the load side of each element relay to the heater with the (2) independant 2500 watt elements. My question is I have 10 awg on a 30 amp breaker running to the controller which then pigtails to feed the line side of both dials. Am I permitted to run 12 from the load side of each dial to each element??Thanks
Yes, you are permitted to run 12 AWG wire from the load side of each dial to each element, provided that the following conditions are met: Ampacity
The 12 AWG wire must be rated for at least 21.6 amps, which is the current draw of each 2500-watt element at 240 volts.
Overcurrent Protection
The 30-amp breaker at the controller provides adequate overcurrent protection for the 12 AWG wire.
Wire Type
Use copper wire rated for at least 90°C (194°F), such as THHN or XHHW wire.The following diagram shows the permitted wiring configuration:10 AWG, 30A Breaker
12 AWG, 21.6A Rating| || |2500W Element 2500W ElementController Dials
Note: Use wire nuts or other approved connectors to make all connections. Ensure that the wire connections at the controller and elements are tight and secure. Inspect the wiring regularly for any signs of damage or wear. Flag for review