Topic: XFMR ground electrode conductor

User: Ranger86, Location: Las Vegas, NV

Asked on: Wednesday, January 5, 2011 at 10:24 am EST
Answered on: Monday, May 13, 2024 at 11:50 pm EDT

Question: Does anyone know at which NEC edition the grounding of separately derived current systems (NEC 250.30) became a requirement?There is an old building (built in 1960) with a number of 480Vdelta-120/208Vwye transformers and the owner wants to know if it was required back then to have a ground electrode conductor installed. I don't have a copy of the 1959 NEC to check this and my experience with the NEC began in 1992....The feeder on the primary side has an equipment ground conductor and the feeder on the secondary side also has an equipment ground conductor but there is no ground electrode conductor installed at the xfmr.Second question,When upgrading a section of a building, Is there a code section that requires the rest of the building to be brought up to current code standards?Thanks for your help.

First Question

The requirement to ground separately derived current systems (NEC 250.30) became effective in the

1968 NEC
. Prior to this, there was no specific requirement in the NEC for grounding separately derived current systems.

Second Question

Yes, there is a code section that requires portions of a building that are being upgraded to be brought up to current code standards.

NEC 110.3(B)
states:> "Electrical equipment and materials installed in existing buildings or structures and not covered by the provisions of this Code shall be permitted to be continued in use if such equipment and materials are maintained in a safe condition."However, this section also states that "If any alteration, extension, or addition is made to an existing electrical installation, the entire installation shall be made to conform to the provisions of this Code, except as noted in 110.3(C)."Therefore, if a portion of a building is being upgraded, the entire installation must be brought up to current code standards, unless otherwise noted in NEC 110.3(C).Since the 1968 NEC required the grounding of separately derived current systems, it is likely that the building in question was not in compliance with the code at the time of installation. However, it may have been grandfathered in under NEC 110.3(B) if it has been maintained in a safe condition. Flag for review