User: VIC1958, Location: Chapel Hill, NC
Asked on: Wednesday, January 5, 2011 at 2:43 pm EST
Answered on: Monday, May 13, 2024 at 11:51 pm EDT
Question: Ok...here I go. Meter is grounded with 8' grounding rod. Circuit breaker box is bonded to meter via conduit. Grounding rod to meter is # 4 wire and is connected to neutral lug in meter box. Circuit breaker box is grounded to cold water pipe at entrance to house. Water meter is jumped with bonding jumper. Grounding wire from cold water pipe to circuit breaker box is connected to the grounding bus bar. The circuit breaker box is bonded to the rest of the system via bonding jumper from the meter conduit lug to the panels neutral buss bar, then from neutral buss bar to the panels bonding buss bar. Is this correct? And is my terminology correct?
Is the Grounding Correct?
Yes, the grounding is generally correct according to the provided information. The meter is grounded with a grounding rod, the circuit breaker box is bonded to the meter via conduit, and the grounding rod is connected to the neutral lug in the meter box.
Is the Terminology Correct? Neutral lug: Correct Grounding bus bar: Correct Bonding jumper: Correct Bonding buss bar: The proper term is "bonding busbar."Additional Notes: It is recommended to use a #6 grounding wire from the grounding rod to the meter. The cold water pipe should be properly grounded by connecting a grounding clamp to the pipe and running a #6 grounding wire to the grounding bus bar in the circuit breaker box. The grounding wire from the cold water pipe to the circuit breaker box should be connected to the grounding bus bar, not the neutral bus bar. The bonding jumper from the meter conduit lug to the panel's neutral bus bar and then to the panel's bonding busbar is correct.Overall, the grounding setup appears to be correct. It is recommended to consult with a qualified electrician to verify and ensure the proper functioning of the grounding system. Flag for review