Topic: Solar PV Grounded Conductor Identification

User: stevee, Location: Massachusetts

Asked on: Wednesday, January 5, 2011 at 5:07 pm EST
Answered on: Monday, May 13, 2024 at 11:52 pm EDT

Question: Does the grounded conductor of a DC output circuit have to be identied by the color white or grey as required in NEC 200.6?Is it permissible to use a colored conductor, let's say black for the grounded conductor?Does the color identification apply to the source circuit conductors also?

  1. Does the grounded conductor of a DC output circuit have to be identied by the color white or grey as required in NEC 200.6?

    No, the grounded conductor in a DC output circuit can be any color except green, green with yellow stripes, or bare. This is because NEC 200.6 only applies to AC circuits.
    2. Is it permissible to use a colored conductor, let's say black, for the grounded conductor?

    Yes, it is permissible to use a colored conductor, such as black, for the grounded conductor in a DC output circuit.3. Does the color identification apply to the source circuit conductors also?

    No, the color identification requirements of NEC 200.6 do not apply to the source circuit conductors in a DC output circuit.