User: Eddy Current, Location: Chapel Hill, NC
Asked on: Wednesday, January 5, 2011 at 8:16 pm EST
Answered on: Monday, May 13, 2024 at 11:53 pm EDT
Question: We hooked up a saw the other day and ran # 10 wire in a 1/2 piece of seal tight 3 foot long. One of the guys that came to check it out before the inspector came said you can't have #10 wire in anything 1/2. Does anybody have a code reference for this?
NEC 2023Chapter 3 Wiring Methods and MaterialsArticle 352 Flexible Metal Conduit352.45 Fill(A) Number of Conductors. The number of conductors permitted in flexible metal conduit shall not exceed the percentage fill specified in Table 352.45(A).
Exception: Where the conduit is not used in a raceway or does not contain conductors of more than four (4) different systems, and where the load is balanced as required in Article 220, the allowable fill is increased to 60 percent.(B) Conductors of Different Systems. Not more than one conductor of any system shall be permitted in a flexible metal conduit containing other conductors of another system unless the conductors of the different systems are separated by a substantial grounded metal barrier. Exception: Where a flexible metal conduit is used as permitted in 300.22 (i.e., for motor leads).Therefore, the claim that #10 wire is not permitted in a 1/2" piece of seal tight is incorrect. Table 352.45(A) shows that #10 wire is permitted in a 1/2" flexible metal conduit with a fill percentage of 40%.
Example: 1/2" flexible metal conduit 3 #10 THHN conductors* Conduit fill: 3 x 0.19 sq.in. / 0.36 sq.in. = 53%Since the actual fill percentage (53%) is within the allowable fill percentage (60%) for balanced loads, the installation is compliant with the NEC. Flag for review