User: Keri_WW, Location: New Jersey
Asked on: Thursday, January 6, 2011 at 7:57 am EST
Answered on: Monday, May 13, 2024 at 11:54 pm EDT
Question: Was on a site visit the other day and ran across a VAV box that had a low voltage (24V) control box mounted to the side of it (basically looks like a big junction box). About 6" in front of it is a truss member. I asked about the box and it supposedly doesn't need regular access, only when there is a problem or a change needs to be made. It is partially accessible, just work around the truss member.My thinking is that this is not my concern (falling under NEC 110.26 requirements) since it appears to me to be an integral part of the VAV equipment. Would you agree that an electrical inspector shouldn't have beef with this? The mechanical inspector on the other hand may...
Electrical Inspector's Perspective
NEC 110.26 (Access to Electrical Equipment) requires that electrical equipment must be accessible for inspection, maintenance, repair, and replacement. The intent is to ensure that qualified personnel can safely and efficiently access and service electrical equipment.In this case, the low voltage control box is considered an integral part of the VAV unit, and as such, it is not subject to the accessibility requirements of NEC 110.
26. This is because the control box is not a separate piece of equipment; it is an integral part of the VAV system and cannot be separated for servicing.Therefore, an electrical inspector should not have an issue with the location of the control box, provided that it is adequately protected from physical damage and is accessible to qualified personnel when necessary.
Mechanical Inspector's Perspective
The mechanical inspector may have concerns about the accessibility of the control box, as it may impede access to other components of the VAV system, such as the damper or air filter. Additionally, the truss member may make it difficult to troubleshoot or replace the control box if necessary.Therefore, the mechanical inspector may suggest relocating the control box to a more accessible location or providing a larger opening in the truss member to facilitate access.
Conclusion:
While an electrical inspector should not have concerns about the location of the control box, it is important to consider the accessibility needs of the mechanical inspector. It is recommended to consult with both electrical and mechanical inspectors to ensure that the location of the control box meets the requirements of both parties. Flag for review