User: mull982, Location: Wisconsin
Asked on: Thursday, January 6, 2011 at 8:32 am EST
Answered on: Monday, May 13, 2024 at 11:54 pm EDT
Question: I'm trying to double check a generator avaliable fault current to that which my software program is giving me. I have the generator specs which gives the generator voltage, kVA, p.f. and all of the impedance paramaters.For the impedance paramaters it gives the synchronous reactance, neg sequence reactance, zero sequence reactance, transient reactance, subtransient reactance, and quadrature reactance.My first question is which of these values I would use to calculate the generator avaliable fault current. I guess this would depend on at what length of time I wanted the fault current for, 1/2 cycle, 5 cycles etc... I'm using skm powertools and I believe it lists the fault current as a 5 cycle current so I'd be interested in finding the 5 cycle fault current. Would I use the transient or synchronous reactance values for this?My second question is the calculation method. All the values listed above are given in p.u. So could I simply take the voltage of the generator to be 1pu and divide one of the above p.u. impedances into the the 1pu voltage to come up with the p.u. current? I could then take this p.u. current and compare it to the base or rated current of the generator to determine the avaliable fault current? Does this sound correct?This generator is listed as a 240/480V generator so I dont know how this effects the way we look at these paramaters or carry out the p.u. calculations?
Answer to Question 1
For a 5-cycle fault current, you would use the
transient reactance (Xd). Transient reactance represents the generator's impedance during the first few cycles of a fault, which is typically around 5 cycles.
Answer to Question 2
Your method for calculating generator available fault current is correct. Here are the steps:1.
Convert the generator voltage to per unit (p.u.)
Divide the generator voltage by the base voltage. For a 240/480V generator, the base voltage is 480V. Therefore, the p.u. voltage is:
2. p.u. voltage = 240V / 480V = 0.5
Calculate the p.u. current
Divide the p.u. voltage by the transient reactance in p.u.:
3. p.u. current = p.u. voltage / Xd (p.u.)
Convert the p.u. current to symmetrical fault current
Multiply the p.u. current by the generator base current (rated current):Symmetrical fault current = p.u. current × generator base current
Note: For a 3-phase generator, the symmetrical fault current would be the same for all three phases. The base current can be found in the generator specifications. Flag for review