Question: If a utility has given its avaliable 3 phase fault current for a facility to be used in a short circuit study is it possible to find or estimate the avaliable L-G fault current from the utility? Can you simply divide the 3phase fault current by 1.73 to get an estimate or must you know the zero sequence impedance from the utility?Someone was trying to tell me that you can simply divide the 3phase fault current by 3 as a rough estimate but I dont believe that is correct?
It is important to understand that the available fault current for a three-phase fault and a line-to-ground (L-G) fault are not simply related by a factor of 1.73 or 3. The relationship between the two depends on the system's grounding configuration and the impedance of the neutral path.In general, the available L-G fault current is lower than the available three-phase fault current because the neutral path provides a lower impedance path for the fault current to flow. However, the exact relationship between the two currents depends on the specific system parameters.If you do not have access to the utility's zero sequence impedance data, you can make a rough estimate of the available L-G fault current by dividing the available three-phase fault current by a factor of 2.5 to 3. This estimate is based on the assumption that the system is effectively grounded and that the neutral path impedance is relatively low. However, it's important to note that this is just an estimate and the actual L-G fault current may vary depending on the system's specific characteristics.It is always best to contact the utility for accurate fault current data. They can provide you with the necessary information to perform a more precise short circuit study. Flag for review