Topic: Flexible Cords in Electrical Equipment Room

User: Crawfish, Location: Ohio

Asked on: Thursday, January 6, 2011 at 9:05 am EST
Answered on: Monday, May 13, 2024 at 11:54 pm EDT

Question: Hello,In a commercial building (highschool) equipment room we have a at$T smartjack that requires 110v and it mounted on a wood back board. We need to plug it into our ups on the other side of the room about 25ft away. Rather than pay for an electrician to tap into an existing 110 and intall a new outlet, is it to code to run a flexible cord from the smart jack which has a 3 prong plug over our wiring rack and into our ups. We may also need to install a few clips on the backerboard to secure the wire a bit before it goes across on the wire rack.Thank you for your timeAaron

National Electrical Code (NEC) Considerations



Article 400.8

Flexible cords and cables shall not be used as a substitute for fixed wiring.


Article 400.11

Flexible cords and cables shall not be run through holes in walls, ceilings, or floors unless approved for such use.

Article 400.12

Flexible cords and cables shall be secured to the surface from which they are suspended by clips, strapping, or other approved means.

Specific to Your Situation

Based on the NEC requirements, using a flexible cord to power the smartjack from the UPS over the wire rack

would not be compliant with the code
. Here are the reasons: The cord would be used as a substitute for fixed wiring, extending its reach beyond the intended use. The cord would be run over the wire rack, which is not an approved method for supporting cables. Securing the cord with clips to the backboard may not provide adequate support and could lead to damage or insulation failure.

Recommended Solution

The best solution would be to have an electrician install a dedicated 110v outlet near the smartjack. This would require tapping into an existing circuit and installing a new electrical box and receptacle.

Additional Considerations:
Make sure the UPS has sufficient capacity to handle the power requirements of the smartjack. Use a high-quality flexible cord if you do decide to go with that option, but be aware that it may not be as durable as fixed wiring.* Label the cord clearly and ensure that it is not a tripping hazard. Flag for review