Topic: Bonding a floor

User: muskrat, Location: St. Louis, MO

Asked on: Thursday, January 6, 2011 at 10:25 am EST
Answered on: Monday, May 13, 2024 at 11:54 pm EDT

Question: The contractor installed Nora Environcare ED(electrostatic discharg?) flooring. It uses a conductive mastic and flooring that has a 3/8" self-adhesive copper foil ribbon (1 per 1000 sq.ft.)(+/- 6" tail curled up above the cove base). Any of you vastly more experienced people ever tried to deal w/ this stuff? There's a 1/4X1" copper bar w/ #6AWG back to service ground 4'AFF directly above it. What are your suggestions to tie copper foil to buss bar(split bolt&#12 solid?):-? The company is NO help

Tying Copper Foil to Copper Bus BarMaterials

Split bolt connector (sized for #6 AWG and 1/4" copper bar) #12 AWG solid copper wire

Steps

1.

Check Continuity

Use a multimeter to verify that the copper foil and the copper bus bar are electrically continuous.2.

Clean Surfaces

Remove any dirt or oxidation from the surfaces of the copper foil and the bus bar.3.

Strip Copper Foil

Strip approximately 1/2" of the copper foil insulation from the end.4.

Wrap Copper Foil

Wrap the stripped end of the copper foil around the copper bus bar.5.

Secure Split Bolt

Place the split-bolt connector over the wrapped copper foil and tighten it securely.6.

Attach Grounding Wire

Connect one end of the #12 AWG copper wire to the split bolt connector.7.

Ground Wire

Route the other end of the grounding wire to the service ground 4' AFF.8.

Verify Grounding

Use a multimeter to verify that the copper foil, bus bar, and grounding wire are all electrically connected to the service ground.

Additional Tips

Curl the 6" tail of the copper foil ribbon up above the cove base and away from any moisture sources. Ensure that the copper foil ribbon is properly adhered to the flooring. Test the grounding system regularly to ensure proper operation.

Caution:
Electrostatic discharge (ESD) flooring should be installed and maintained by experienced professionals. Avoid touching the copper foil with bare hands, as oils and dirt can affect conductivity. Follow all manufacturer's instructions and local building codes when installing and grounding ESD flooring. Flag for review