Question: The contractor installed Nora Environcare ED(electrostatic discharg?) flooring. It uses a conductive mastic and flooring that has a 3/8" self-adhesive copper foil ribbon (1 per 1000 sq.ft.)(+/- 6" tail curled up above the cove base). Any of you vastly more experienced people ever tried to deal w/ this stuff? There's a 1/4X1" copper bar w/ #6AWG back to service ground 4'AFF directly above it. What are your suggestions to tie copper foil to buss bar(split bolt solid?):-? The company is NO help
Tying Copper Foil to Copper Bus BarMaterials
Split bolt connector (sized for #6 AWG and 1/4" copper bar) #12 AWG solid copper wire
Steps
1.
Check Continuity
Use a multimeter to verify that the copper foil and the copper bus bar are electrically continuous.2.
Clean Surfaces
Remove any dirt or oxidation from the surfaces of the copper foil and the bus bar.3.
Strip Copper Foil
Strip approximately 1/2" of the copper foil insulation from the end.4.
Wrap Copper Foil
Wrap the stripped end of the copper foil around the copper bus bar.5.
Secure Split Bolt
Place the split-bolt connector over the wrapped copper foil and tighten it securely.6.
Attach Grounding Wire
Connect one end of the #12 AWG copper wire to the split bolt connector.7.
Ground Wire
Route the other end of the grounding wire to the service ground 4' AFF.8.
Verify Grounding
Use a multimeter to verify that the copper foil, bus bar, and grounding wire are all electrically connected to the service ground.
Additional Tips
Curl the 6" tail of the copper foil ribbon up above the cove base and away from any moisture sources. Ensure that the copper foil ribbon is properly adhered to the flooring. Test the grounding system regularly to ensure proper operation.
Caution: Electrostatic discharge (ESD) flooring should be installed and maintained by experienced professionals. Avoid touching the copper foil with bare hands, as oils and dirt can affect conductivity. Follow all manufacturer's instructions and local building codes when installing and grounding ESD flooring. Flag for review