Question: Friends, Given a tfmr 480 volt primary / 120/208 volt secondary. If you connect a neutral from the primary source to XO and the neutral from the secondary (load) to XO what effect would it have on the circuit?
Connecting a neutral from the primary source to the neutral from the secondary would create a direct electrical connection between the primary and secondary windings of the transformer. This would effectively short-circuit the primary winding and cause a large amount of current to flow through the transformer. This would likely cause the transformer to overheat and fail.In addition, connecting the neutrals together would defeat the purpose of the transformer's isolation. The transformer is designed to provide electrical isolation between the primary and secondary windings, so that faults on the secondary side do not affect the primary side. Connecting the neutrals together would eliminate this isolation and allow faults on the secondary side to affect the primary side.For these reasons, it is important to never connect the neutrals of a transformer's primary and secondary windings together. Flag for review