Question: So I have a client that is wanting to hook up a Lincoln Electric Precision Tig 275. The recommended input wire and fuse size chart recommeneds a 150 amp breaker with #3 conductors and a #6 ground. Am I missing something here? That is no where near enough from what I see. This will be fed with a subfeed cable. What are your thoughts? The following is a link to the chart. It is the 230/1/60 voltage and go across to the right hand chart. "For unbalanced AC TIG welding above 275 amps".http://content.lincolnelectric.com/pdfs/products/navigator/im/IM702.pdf
Required Line Size and Breaker
The recommended input wire and fuse size chart for the Lincoln Electric Precision TIG 275 is correct for the specific conditions stated: Balanced AC TIG welding below 275 amps
For unbalanced AC TIG welding above 275 amps, the following line sizes and breaker are required
Conductors
#1 AWG stranded copper
Ground
#2 AWG stranded copper
Breaker
250 amp, Type HACR
Reasoning
Unbalanced AC TIG welding creates a significant current imbalance between the two line conductors and the neutral conductor. This imbalance requires larger line sizes and a higher breaker rating to safely handle the increased current flow.
Subfeed Cable
If a subfeed cable is used, it must be sized appropriately for the required current and voltage. The subfeed cable must meet or exceed the specifications outlined above (#1 AWG for conductors and #2 AWG for ground).
Additional Notes: The provided link does not include the recommended line sizes and breaker for unbalanced AC TIG welding above 275 amps. It is important to consult with a qualified electrician to ensure that the electrical system is capable of handling the increased current load.* Oversizing the line sizes and breaker will provide additional safety and protection for the welding equipment and electrical system. Flag for review