Topic: Nec 450.5

User: LYLE2231, Location: Logan, Utah

Asked on: Thursday, January 6, 2011 at 12:30 pm EST
Answered on: Monday, May 13, 2024 at 11:55 pm EDT

Question: Friends, would NEC 450.5 (A) (2) be the correct article to apply to calc OCP for 30kva dry transformer?

Yes, NEC 450.5 (A)(2) is the correct article to apply to calculate the OverCurrent Protection (OCP) for a 30kVA dry transformer.NEC 450.5 (A)(2) states that "transformers shall be protected by an individual overcurrent device on the primary side, rated or set at not more than 125 percent of the rated primary current of the transformer."For a 30kVA dry transformer, the rated primary current can be calculated as follows:Primary current (Ip) = transformer kVA / (1.732 primary voltage)Assuming a primary voltage of 480 volts, the primary current would be:Ip = 30 kVA / (1.732 480 V) = 38.4 ATherefore, the OCP for the 30kVA dry transformer should be rated or set at not more than 125% of 38.4 A, which is 48 A. Flag for review