Question: Can I use the critical branch circuit in a nursing home to supply power to the transformers feeding the card/door axcess system. I do not have the code in front of me but in health care facility critical branch A6 says other funtions for normal hospital operation. Can I consider card axcess normal operation?Thanks.
NFPA 101: Life Safety CodeSection 7.10.
3.1.6(2) Critical Branch Circuit7.10.
3.1.6.2 Functions. The critical branch circuit shall supply power to the following functions:(a) Illumination system(b) Alarm system(c) Exit signs and lights(d) Smoke detectors and control system(e) Fire alarm system(f) Other functions that are necessary for normal hospital operation, including those above, as determined by the AHJInterpretation
"Normal hospital operation" includes functions that are essential for the daily operation of a healthcare facility. Access control systems, including card/door access systems, are typically considered essential for the daily operation of a healthcare facility.* Therefore, it is generally acceptable to supply power to the transformers feeding the card/door access system from the critical branch circuit.
However, the final determination should be made by the Authority Having Jurisdiction (AHJ) based on the specific circumstances of the healthcare facility. Flag for review