Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Tap conductor feeding primary side of transformer

User: lpfam11, Location: Tennessee

Asked on: Thursday, January 6, 2011 at 10:49 pm EST
Answered on: Monday, May 13, 2024 at 11:57 pm EDT

Question: I have a situation and am having a hard time coming up with a solution because of NEC 240.21.I have a 2250A feeder. It is 297 volts (yes, 297 volts). I need to bring tap conductors off of it to feed a small transformer (also 297 volts) in a mini power zone center. There small transformer has a 40A breaker on the primary side.The problem I have is that according to NEC 240.21, my tap conductors coming off of the 2250A feeder must be no less than 1/3 the rating of the over current protection device protecting the feeder which in my case is a 2500A fused bolt switch. That tells me that my tap conductors must be suitable for no less than 825 amps which means running (at a minimum) parallel 600 kcmil cables as my tap conductors.This will not work for me because the breaker that feeds the small transformer is only 40A. You cannot fit 600 kcmil cables into the lugs on a 40A breaker.My question is, does anyone have a way around this particular code or is there something else I can do that will allow me to run smaller cables over to the 40A breaker?Any help is much appreciated.

Possible Solutions



1. Derating the Feeder

Derate the 2250A feeder to 825A in accordance with NEC Article 310.15(B)(3). This will allow you to size the tap conductors based on an 825A rating.

2. Installing a Sub-Panel

Install a sub-panel (fused or circuit breaker) downstream of the 2250A feeder. Connect the tap conductors to the sub-panel and install a 40A breaker in the sub-panel to protect the small transformer.

3. Using a Transformer

Install a step-down transformer with a primary winding rated for 825A and a secondary winding rated for 40A. Connect the tap conductors to the 825A primary winding and connect the 40A secondary winding to the small transformer.

4. Special Permission

Request special permission from the local authority having jurisdiction. Provide documentation demonstrating the specific situation and the safety measures you intend to implement.

Notes:
All solutions should comply with the applicable electrical codes and standards. Consult with a qualified electrician to ensure proper installation and safety. If you choose to derate the feeder, you may need to adjust the overcurrent protection devices accordingly. The tap conductors should be securely connected and protected from physical damage. Flag for review

Previous Question Next Question