Topic: Manufacturers Specs vs. NEC

User: dlalonde, Location: Massachusetts

Asked on: Friday, January 7, 2011 at 11:20 am EST
Answered on: Monday, May 13, 2024 at 11:57 pm EDT

Question: A 45kva dry type transformer was installed inside with an underground conduit feeding the primary.This conduit has no mechanical connection to the enclosure.The vents on the bottom of the transformer have been cut out (with what looks like a shovel)to allow the conduit to enter the enclosure.There is however a bonding bushing with a ground wire attached to the enclosure .I would see this install as a violation of 08-300.10 .The manufacturers spec state that this is an acceptable location to enter this enclosure.I dont see how this vented area will accept the locknuts and create a metallic connection to comply with this code.Thanks for any input you may have.

Code Violation

NEC 08-300.10 requires that the conduit or cable entering an enclosure for electrical equipment be mechanically connected to the enclosure by a threaded coupling or an approved connector.

Manufacturer's Specification

The manufacturer's specification stating that the conduit entry through the cut-out vents is acceptable does not override the code requirement. The code requirement takes precedence.

Lack of Metallic Connection

The cut-out vents do not provide a suitable surface for creating a proper metallic connection with the locknuts. It is unlikely that the locknuts will be able to engage securely with the uneven surface, creating a potential safety hazard.

Potential Problems

The cut-out vents compromise the integrity of the transformer's enclosure, potentially allowing moisture or debris to enter. The lack of a proper metallic connection could lead to loose connections and overheating, increasing the risk of electrical fires. The unsecured conduit could cause damage to the transformer or its components.

Conclusion

Based on the information provided, the installation appears to violate NEC 08-300.10. The cut-out vents do not provide a suitable surface for a proper metallic connection, posing a safety hazard. The installation should be corrected to comply with the code requirement.

Recommended Solution:
Install a conduit body with a threaded connection to the transformer enclosure. Secure the conduit to the conduit body using a locknut. Ensure that the conduit is properly supported and secured throughout its length.By following these recommendations, the installation will be compliant with the code and the safety concerns associated with the cut-out vents will be mitigated. Flag for review