User: KMark5710, Location: Logan, Utah
Asked on: Friday, January 7, 2011 at 11:24 am EST
Answered on: Monday, May 13, 2024 at 11:58 pm EDT
Question: Had an electrical contractor stop by and ask this question today. He has a 480-volt panel with a shunt trip breaker. The controls for the shunt trip breaker are 120-volt. He wanted to know if that would be an issue. He was concerned about having 120-volts present in the 480-volt panel whenever someone turned off the panel's main breaker. Any thoughts? Where can I find this in the code?My immediate response was to place a warning tag about control power being present.
Yes, this is a potential issue.Code Reference
NEC 110.26(E) prohibits keeping energizing equipment or circuits in a switchboard with a device that is disconnected, unless the energized equipment or circuits are essential to the operation of the switchboard.
Explanation
The 120-volt control power for the shunt trip breaker creates a potential hazard if it remains energized after the 480-volt main breaker is turned off. This is because:
Shock hazard
Live 120-volt wiring could be present in the panel, even when the main breaker is off.
Insulation breakdown
The insulation on the 120-volt wiring could break down over time due to the presence of high-voltage equipment. This could lead to an electrical fault or fire.
Solution
There are two main solutions to this issue:
Isolate the 120-volt control power
Install a separate disconnect switch or circuit breaker for the 120-volt control power. This will allow it to be isolated when the 480-volt main breaker is turned off.*
Install a warning tag
As you suggested, a warning tag can be placed on the panel indicating that control power is present even when the main breaker is off. This will alert personnel to the potential hazard.
Recommendation:
The best solution is to isolate the 120-volt control power. This provides the highest level of safety and code compliance. If this is not feasible, a warning tag should be used as a minimum safety measure. Flag for review