Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: ATS normal source disconnect

User: mjmike, Location: Illinois

Asked on: Friday, January 7, 2011 at 4:52 pm EST
Answered on: Monday, May 13, 2024 at 11:59 pm EDT

Question: I have an outside generator with an outside transfer switch serving a piece of outdoor equipment. The normal power source is derived from inside the building the outdoor equipment serves. I have a disconnect inside the generator enclosure, but do I need a disconnect at the transfer switch for the normal source? This is kind of like section 700.12(B)(6) but the opposite if you know what I mean.

Yes, a disconnect is required at the transfer switch for the normal source.

Section 700.12(B)(6) requires a disconnecting means for each feeder over 1000 volts, nominal, that is connected to an outside generator. This requirement does not apply to the generator itself, but it does apply to the feeders that connect the generator to the building or structure being served.In this case, the normal source is connected to the building or structure being served, and the generator is connected to the building or structure through the transfer switch. Therefore, a disconnecting means is required for the normal source at the transfer switch.The disconnecting means can be a circuit breaker, a fuse, or a switch. The disconnecting means must be rated for the voltage and current of the normal source, and it must be accessible to qualified personnel. Flag for review

Previous Question Next Question