User: Gibbs, Location: Chapel Hill, NC
Asked on: Friday, January 7, 2011 at 4:56 pm EST
Answered on: Monday, May 13, 2024 at 11:59 pm EDT
Question: I see on some blogs inspectors are requiring fuzes (NEC 450.3(B)) to be on the primary of doorbell transformers. Aren't they excempt from fuze requirement by NEC 450 excption#2?
Yes, doorbell transformers are exempt from the fuse requirement by NEC 450 Exception #2.NEC 450.3(B) requires that transformers have primary fuses unless they are of the dry-type and have a 250VA or less rating.NEC 450 Exception #2 exempts doorbell transformers from this requirement.Therefore, doorbell transformers do not require primary fuses. Flag for review