Question: I was asked to give an estimated running cost of operating a 3 phase 75 HP motor for 80 hrs. I assumed at 480 Vac that the motor would have roughly 100 FLA.My equation then became KW = 480 V * 100 A * 1.732 / 1000 (ignored power factor and demand) and came to roughly 83 KW.I had a coworker check to verify my answer and he used a different method. He used 1 HP = .746 KW and came to roughly 56 KW. Does motor phase affect this equation?Which method is correct when solving for KW in a three phase system and why?Any insight would be apprecciated, Thanks.
Method 1 (Your Equation)
This method uses the three-phase power formula: `KW = 1.732 V I PF`, where PF (power factor) is assumed to be 1. This method is more accurate as it considers the three-phase nature of the motor. Your coworker's method does not account for the three-phase factor of 1.732, which is a critical factor in calculating power in three-phase systems.KW = 480 V 100 A 1.732 / 1000 = 83.23 KW
Method 2 (Your Coworker's Method)
This method assumes single-phase power, which is not suitable for a three-phase motor.* This method significantly underestimates the actual power consumption of the motor.KW = 75 HP 0.746 KW/HP = 56 KW
Conclusion
The correct method for calculating the KW of a three-phase motor is
Method 1, which takes into account the three-phase factor. The answer you obtained (83.23 KW) is a more accurate estimate of the motor's power consumption.
Motor Phase:
Motor phase does affect the power formula. In three-phase systems, the power formula involves a factor of 1.732, which is not used in single-phase systems. Therefore, it is essential to consider the motor phase when calculating power consumption. Flag for review