Topic: Class 2 device..UL listing Necessary?

User: Speirick, Location: 3 Hr 2 Min from Winged Horses

Asked on: Friday, January 7, 2011 at 7:08 pm EST
Answered on: Monday, May 13, 2024 at 11:59 pm EDT

Question: I have a Class 2 circuit board switching 24 volt contacts. My inspector is telling me that all equipment needs to be Listed or Approved. He's referencing article 110.2.I know a lot of people say that "Power Limited" devices don't need to be listed.anyone have a Code article showing this?Article 725.1 FPN shows some "differentiation" from Class 1 circuits etc but i don't see "equipment" there.any help is appreciated.Steve

Article 100 Definition of "Listed"

"Listed" means included in a list published by an organization that is acceptable to the authority having jurisdiction and concerned with evaluation of products or services, that maintains periodic inspection of production of listed equipment or materials, and whose listing states either that the equipment or material meets appropriate designated standards or has been tested and found suitable for a specified purpose."

Article 725.1 (FPN)

"Control and signaling circuits are recognized as separate from power circuits by having both of the following characteristics:a. The field-wiring terminals of control and signaling circuits do not carry sufficient voltage or energy to constitute a shock hazard.b. The control and signaling circuits are installed to prevent any difference in potential between field-wiring terminals and the building ground."

Interpretation:


Based on the above definitions and FPN, "Power Limited" devices used in Class 2 circuits are not required to be Listed or Approved if they meet the following criteria: The field-wiring terminals do not carry sufficient voltage or energy to constitute a shock hazard. The circuits are installed to prevent any difference in potential between field-wiring terminals and the building ground.It is important to note that the inspector may have additional requirements based on local codes or interpretations. It is recommended to consult with the local authority having jurisdiction to confirm the requirements for your specific installation. Flag for review