Topic: Lighting Flicker

User: cdcengineer, Location: MA

Asked on: Friday, January 7, 2011 at 7:41 pm EST
Answered on: Monday, May 13, 2024 at 11:59 pm EDT

Question: Folks, I got a strange phenomena happening at the house. My lights are flickering when certain loads are turned on. It doesn't seem to matter which phase these loads are on or whether it's a cord and plug load placed in any room.I spent some time as a licensed repair tech and thought I'd seen this before. It usually always ends up as a loose neutral. I checked the panel (main and branch ckt's), but no solution. I called a friend at the utility and they came down and checked the connection on the transformer - A-OK. I don't have any voltage drop issue, and the house hasn't had any recent repair and/or modification. We've lived here for over (6) years. Voltage measurements from A to neutral 108V, B to neutral 135V with all loads on. With all loads off, we have 124V (A Phase) and 120V (B Phase).I'm cracking up a bit. I've pulled every device on circuits in the rooms with flicker) to verify connection. I've tightened the connections in the meter housing, checked the grd'g electrode conductor connection.Without typing for another page or so, does anyone want to toss out any ideas?Thx,CDC

Possible Causes



Loose neutral outside the panel

Check the neutral connection at the service entrance where the utility line enters the building.


Overloaded circuit

Verify that all circuits are properly sized for the loads they are carrying.

Faulty appliance or device

Test all appliances and devices that coincide with the flickering to identify any that may have loose internal connections or other issues.


Ground fault

Check for ground faults using a ground fault circuit interrupter (GFCI) or by measuring the voltage between the neutral and ground.

Capacitor bank imbalance

If there are capacitor banks installed on the secondary side of the transformer, an imbalance between them can cause voltage fluctuations.


Arcing or sparking

Inspect for any arcing or sparking at connections, outlets, switches, or loose wires.

Voltage regulation issues

Contact the utility company to investigate any potential issues with the voltage regulation on their system.

Troubleshooting Tips:
Use a voltage meter to measure voltage levels at different points in the electrical system under various load conditions. Inspect all wiring connections, paying close attention to neutral connections. Disconnect all loads and turn them on one by one to isolate the source of the flickering. If possible, use a load analyzer to monitor the current draw and power factor of loads. Consider installing a voltage regulator to stabilize the incoming voltage. Flag for review