Topic: 3-Phase rectification & Ripple

User: SG-1, Location: Ware Shoals, South Carolina

Asked on: Friday, January 7, 2011 at 11:28 pm EST
Answered on: Tuesday, May 14, 2024 at 12:00 am EDT

Question: I need a formula to calculate the AC ripple for an unfiltered 3-Phase Bridge ( 6 pulse ). The only formulas I can find are for circuits with a smoothing capacitor.Maybe I could just use an ungodly small capacitor for the calculation...??The final intent of this exercise is to be able to measure the ripple to determine the health of the diode bridge. The supply is variable 0 - 300 VDC.

Formula for AC Ripple for Unfiltered 3-Phase Bridge (6 Pulse)

AC Ripple = (Vdc  π / 3  √2) / (2  π  f  L)
where: Vdc is the DC output voltage π is the mathematical constant approximately equal to 3.14 f is the frequency of the AC input voltage* L is the inductance of the load

Note

This formula does not include the effect of any smoothing capacitor.

Using an Ungodly Small Capacitor

Using an ungodly small capacitor to approximate the unfiltered case is not a reliable method. An extremely small capacitor would have negligible ripple-reducing effect, and the formula would still not accurately represent the behavior of a truly unfiltered circuit.

Determining Diode Bridge Health from AC Ripple:


Measuring the AC ripple can indicate the health of the diode bridge if you observe a significant increase in ripple compared to the expected value. However, other factors can also affect the AC ripple, such as the load characteristics and the presence of harmonics in the AC input voltage. Therefore, it is essential to consider multiple factors when assessing the health of the diode bridge based on AC ripple measurements. Flag for review