Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Generator install question.

User: Saywatt, Location: Massachusetts

Asked on: Saturday, January 8, 2011 at 10:37 am EST
Answered on: Tuesday, May 14, 2024 at 12:01 am EDT

Question: Looking to install a 20kw generator at a home that has a 3-wire service to a 200amp MB panel.The ATS is service rated with a 200amp breaker/dico. that I'm installing between the meter and the panel.Does the service to the panel then become a feeder? Do I need to replace the 3-wire seu with 4-wire ser and separate the grounds and neutrals?

Service to Panel

Once the ATS is installed, the service to the panel becomes a feeder since it is now being supplied by the generator instead of the utility.

4-Wire Service

Yes, you need to replace the 3-wire SEU (Service Entrance Underground) cable with 4-wire SER (Service Entrance Rating) cable. The 4-wire cable will provide separate paths for the neutral and grounding conductors.

Ground and Neutral Separation

Yes, you need to separate the grounding and neutral conductors. The grounding conductor will be connected to the ground rod and the neutral conductor will be connected to the neutral bar in the panel.

Requirements



ATS Rating

The ATS should be rated for the full load of the generator (20kW in this case).


Main Breaker

Install a 200A main breaker in the ATS.

Feeder Cable

Use a 4-wire SER cable sized appropriately for the load and distance.


Ground Rod

Install a ground rod in accordance with local codes.*

Neutral Bar

Ensure that the panel has a separate neutral bar for connecting the neutral conductors.

Procedure:
1. Disconnect power from the panel.
2. Install the ATS between the meter and the panel.3. Replace the 3-wire SEU cable with 4-wire SER cable.
4. Separate the grounding and neutral conductors.5. Connect the grounding conductor to the ground rod and the neutral conductor to the neutral bar in the panel.
6. Turn on power from the generator and verify proper operation of the ATS.7. Have the work inspected by a qualified electrician to ensure code compliance. Flag for review

Previous Question Next Question