Question: I have a situation where I am replacing an outdoor inground pool subpanel. There has been no bonding installed at the pump, gas heater, and bubbler for the spa. The homeowner found the original contract from Sylvan when the pool was installed that stated that all the pool bonding would be done and the bond wire would be left stubbed out "for the home-owner's electrician to complete". It was dated October 1979. It did get inspected at the time. The equipment has been replaced since then. I looked in the service to see if the "home-owners electrician" had run the bond wire there and he hadn't. Can anyone tell me what the bonding requirements were in 1979? There is no bond wire visible at the equipment. Now I have an uptight customer.Thanks, Steve

Bonding Requirements in 1979

The National Electrical Code (NEC) has undergone numerous revisions since 1979. However, the following requirements were in place during that time for swimming pools: Section 680-26(a) required that all metal parts of the pool structure, including the pool shell, deck, and diving board, be electrically bonded together and grounded. Section 680-26(b) required that all electrical equipment within 5 feet of the pool edge, including pumps, filters, and heaters, be bonded to the pool structure and grounded.

Current Bonding Requirements

The current NEC (2020 edition) contains similar bonding requirements for swimming pools: Section 680.26(A) requires that all metal parts of the pool structure, including the pool shell, deck, and diving board, be electrically bonded together and grounded. Section 680.26(B) requires that all electrical equipment within 5 feet of the pool edge, including pumps, filters, and heaters, be bonded to the pool structure and grounded.Additionally, the NEC now requires that a bonding grid be installed beneath the pool liner to ensure that the entire pool structure is bonded together.

Implications for Your Situation

Based on the information you provided, it appears that the original pool installer failed to complete the bonding as specified in their contract. This would have been a violation of the NEC at the time, and it remains a violation under the current NEC.The homeowner is justified in being concerned about the safety of the pool, and it is essential that you address the bonding issue promptly.

Recommended Actions Install Bonding Wire

Run a bonding wire from the pool structure to each piece of equipment that is required to be bonded. This includes the pump, gas heater, and bubbler.


Ground the Bonding Wire

Connect the bonding wire to the grounding electrode system of the house.

Inspect the Bonding

Once the bonding is installed, inspect the connections and verify that they are secure and that the bonding wire is continuous.

Communication with Customer
Explain the bonding requirements to the customer and show them the relevant sections of the NEC. Inform them that the pool was not installed in accordance with the original contract and the NEC. Assure them that you are taking steps to correct the issue and ensure the safety of the pool.By addressing the bonding issue, you will be protecting your customer and meeting the requirements of the NEC. Flag for review