Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: 110.26(a)

User: chris kennedy, Location: Miami Fla.

Asked on: Saturday, January 8, 2011 at 4:29 pm EST
Answered on: Tuesday, May 14, 2024 at 12:01 am EDT

Question: Would you consider a dry type transformer, 480V delta - 208y/120 with no OCPD's or controls installed in the transformer enclosure to fall under 110.26?Thanks.

No, a dry type transformer, 480V delta - 208y/120 with no OCPD's or controls installed in the transformer enclosure does not fall under 110.26 of the NEC.
110.26 covers the installation of transformers rated over 600 volts. The transformer you described is rated at 480 volts, which is not over 600 volts. Therefore, 110.26 does not apply to this transformer.The transformer you described must be installed in accordance with the requirements of Article 450 of the NEC. Flag for review