User: jc&sons, Location: 3 Hr 2 Min from Winged Horses

Asked on: Sunday, January 9, 2011 at 2:16 pm EST
Answered on: Tuesday, May 14, 2024 at 12:02 am EDT

Question: if i install a spa on a concrete deck is this spa required to be bonded to steel? this spa is a 50 amp 2pole with gfci protection 4 wire. can someone tell me if tthis is correct.

Bonding Requirements for Spas

Yes, a spa installed on a concrete deck must be bonded to steel. According to the National Electrical Code (NEC), all spas and hot tubs must be bonded to the grounding electrode system.

Grounding Electrode System

The grounding electrode system includes the following components: Metal water pipe in direct contact with the earth for at least 10 feet Metal frames of the building or structure Concrete-encased electrodes that are at least 20 feet long and 2 inches in diameter

Bonding Methods

The spa can be bonded to the grounding electrode system using one of the following methods:
A copper bonding wire sized according to NEC Table 250.122 A metal conduit that connects the spa to an equipment grounding conductor A metal bonding strap that connects the spa to the grounding electrode

Wiring requirements for a 50 amp, 2-pole, 4-wire spa with GFCI protection



Circuit Breaker or Fuse

50 amp, 2-pole


Conductors

4 AWG copper (2 hot, 1 neutral, 1 ground)

Conduit

If the wires are not protected in a wall, ceiling, or floor, they must be run in electrical conduit.

Additional Notes:
The GFCI protection should be located near the spa, within easy reach and no more than 6 feet from the spa.* The spa must be installed by a qualified electrician in accordance with all applicable electrical codes and safety regulations. Flag for review