User: patpappas, Location: Chapel Hill, NC

Asked on: Monday, January 10, 2011 at 8:03 am EST
Answered on: Tuesday, May 14, 2024 at 12:02 am EDT

Question: A relative of mine had electrical work done, new 200A service, the contractor installed the service ground, #4 copper, ran it outside then split the conductor in half by unwinding the strands and attached each smaller wire to seperate ground rods, I asked my realitive why, he did not know why it was done, I have never heard of doing that, don't sound right, it apparently passed inspection. Any thoughts.

Splitting a single ground conductor into two smaller conductors is not in accordance with the National Electrical Code (NEC). The NEC requires that the grounding electrode conductor (GEC) be a single, continuous conductor.

NEC Article 250.64(C) states:> The grounding electrode conductor shall be a single continuous conductor. Where the grounding electrode conductor is connected to the grounded service conductor, the connection shall be made at or as near as practicable to the service entrance. The grounding electrode conductor shall be run with the supply conductors from the service entrance to the grounding electrodes.NEC Article 100 defines a continuous conductor as:> A conductor without splice, tap, or joint.Splitting the GEC into two smaller conductors effectively creates a splice in the GEC, which is not permitted.

Possible Reasons for Doing This Incorrectly



Lack of knowledge

The electrician may not have been aware that splitting the GEC is not allowed.


Space constraints

There may not have been enough room in the conduit or panel to run a single #4 conductor.

Incorrect materials

The electrician may have used a #4 conductor that was not rated for use as a GEC. A GEC must be bare copper or insulated copper with a green or bare outer layer.

Potential Safety Concerns

A spliced GEC can create a weak point in the grounding system, potentially leading to ground faults or electrical shocks.* If the spliced GEC is not properly secured, it could come loose and disconnect, which would eliminate the grounding path for the electrical system.

What Should Be Done:


The incorrect installation should be corrected by removing the spliced GEC and installing a single, continuous #4 GEC in accordance with the NEC. The inspector should be notified of the correction. Flag for review