User: elec_eng, Location: NE Arkansas
Asked on: Monday, January 10, 2011 at 9:16 am EST
Answered on: Tuesday, May 14, 2024 at 12:02 am EDT
Question: The existing building had 120/240V 1ph service and now is being upgraded to 120/208V 3ph service...Electrician is suggesting reusing all existing 120/240V 1ph rated panels by backfeeding from 120/208V. Is this not a code violation? All labels on panels are 120/240 but the actual power supply will be 120/208V. I couldn't find the right code section for this. Thanks.
NEC 2020 Code Section 408.3(B) states that:_Panelboards shall be marked with the voltage and number of phases of the system for which they are designed._Therefore, it is a code violation to reuse 120/240V 1ph panels with a 120/208V 3ph service. The panelboards must be replaced with panels rated for 120/208V 3ph service and labeled accordingly. Flag for review