Topic: Hard Wire for Dish Washer

User: Little Bill, Location: Tennessee NEC:2017

Asked on: Monday, January 10, 2011 at 10:59 am EST
Answered on: Tuesday, May 14, 2024 at 12:03 am EDT

Question: I hope this doesn't appear that I'm changing subjects/threads but since the DW space was mentioned, I will ask. In my area DW are not allowed cord connected. All of the ones that I have replaced just have about 3' of NM run through the wall or floor and laying loose on the floor. How do you guys plan/rough/wire for a hard wired DW? Is the loose NM allowed? Or does it need to be MC or other armored cable?

Hard-Wiring a Dishwasher

In areas where dishwashers are not allowed to be cord-connected, the following steps outline the proper planning, rough-in, and wiring techniques

Planning:
Determine the location of the dishwasher and identify nearby power sources. Plan the routing of the electrical circuit, including the location of outlets, switches, and junction boxes.

Rough-In

Install a dedicated 15A, 120V circuit for the dishwasher. Run NM cable through the walls or floor to the dishwasher location. Provide 3-5 feet of slack cable beyond the dishwasher connection point.

Wiring

Connect the NM cable to a junction box located near the dishwasher. Install a 15A, 120V duplex receptacle inside the junction box. Remove the cover plate from the junction box and connect the dishwasher power cord to the receptacle. Cap and secure any unused cable ends inside the junction box.

NM Cable Requirements

While some jurisdictions may allow loose NM cable to connect the dishwasher, it is generally not recommended for safety reasons. The National Electrical Code (NEC) requires the following:


Section 400.8(3)
: Electrical equipment shall not be connected by flexible connections except as permitted in 400.7 or where specifically permitted elsewhere in this code. Section 400.9

Flexible cords shall not be used as a substitute for the fixed wiring of a structure.

Alternative Cable Options

If loose NM cable is not permitted, alternative cable options include:


Metal Clad Cable (MC) or Armored Cable

These cables provide better protection from physical damage and are more suitable for use in exposed locations.*

Surface-Mounted Raceway

A channel or conduit that can be installed on the surface of walls or floors to enclose and protect the NM cable.

Note:
Always consult with local building codes and electrical inspectors for specific requirements in your jurisdiction. Flag for review