Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Arc Flash vs Gear Interrupting Ratings vs Labeling

User: sparkyguy545, Location: Covington, WA.

Asked on: Monday, January 10, 2011 at 1:29 pm EST
Answered on: Tuesday, May 14, 2024 at 12:03 am EDT

Question: Difficult to answer question.I'm a Consulting Engineer. Virtually 99% of the time, POCO's won't give REAL available fault currents. The numbers they give us "surprisingly" work out to nothing more than the xfmr Z with infinite primary bus reflected to the secondary (our SE). OK, they want to cover their butts so that we adequately provide interrupting gear that exceeds the worst-case. However, a very different (dangerous) thing happens when you do an Arc Flash Study. It is totally counter-intuitive, but often a higher supply fault current will CLEAR faster than a much-smaller service. The opposite is that a lower fault current will often result in a HIGHER hazard than a larger fault current because it will burn-longer (take longer to clear). The formula's are only as good as what data they are provided. However, when we base ALL our computations and ALL our labeling on an unrealistically (but unverifiable) figure from a utility EVERYTHING we calculate and label will ultimately be wrong. The result is that a higher hazard may actually exist because the utility gave us an unrealistically large fault current. After all it NEVER is actually an infinite primary bus.How do others reconcile this conundrum when calculating Arc-Flash data and labeling?

Strategies for Reconciling Utility-Provided Fault Currents in Arc Flash Studies



1. Request Corrected Fault Current Data

Contact the utility and explain the importance of accurate fault current data for arc flash studies. Request corrected values that represent the actual fault currents at the point of use.

2. Utilize Measured Data

Perform on-site fault current measurements to obtain real-world data. This can be done using a secondary injection test or a fault current analyzer.

3. Use Industry Standards and Recommendations

Refer to industry standards such as IEEE 1584 and NFPA 70E for guidelines on estimating fault currents. Consider using conservative fault current assumptions by multiplying the utility-provided value by a safety factor.

4. Perform Sensitivity Analysis

Calculate arc flash hazard levels using different fault current values to determine the impact on the results. This can help identify potential discrepancies and conservative approaches.

5. Consider Utility Distribution System Changes

Be aware of any planned or ongoing changes to the utility's distribution system that may affect fault currents. Regularly update arc flash studies as needed.

6. Document Assumptions

Clearly document the assumptions and data sources used in the arc flash study. This will provide transparency and justification for the results.

Recommended Labeling Approach

Use the most conservative fault current estimate, considering both utility-provided and measured data. Label all equipment with the maximum potential fault current and calculate the corresponding arc flash hazard category. Include a note on the label stating that the fault current value is estimated and may vary from actual conditions.

Additional Considerations:
Recognize that arc flash study results are inherently probabilistic and subject to uncertainties. Encourage regular maintenance and inspection of electrical equipment to minimize arc flash risks. Consider using personal protective equipment (PPE) beyond the calculated arc flash hazard category to provide an additional layer of safety. Flag for review

Previous Question Next Question