Question: I recall a couple odd questions that haunt me still;1) Several motors -fused with an inverse time delay breaker. The largest motor was also 5 minute intermittent duty cycle.Not sure if I took the largest motor at 125% and ignored the 110% intermittent duty deration, or not, at this point. What to do if I see this in the world?2) Multi Family Optional. The question said no house load and no laundry.Would that mean no additional laundry room load on the house load after totalling the units' load? Or no laundry figured in the per units' calc? Does it mean no dryer too? The dryer was not listed and not mentioned at all!
1) Several Motors - Inverse Time Delay Breaker Determine the largest motor in the group
This will be the motor with the highest horsepower or current draw.
Apply 125% demand factor to the largest motor
This accounts for the starting surge current of the motor.
Ignore the 110% intermittent duty deration
Inverse time delay breakers do not provide short-term overcurrent protection, so the intermittent duty cycle can be neglected.
Sum the total demand for all motors
Add the 125% demand of the largest motor to the demand of the other motors.
Compare to the breaker rating
Ensure that the total demand is less than or equal to the rating of the inverse time delay breaker.
2) Multi-Family Optional - No House Load and No Laundry No House Load
This means that no additional load allocation should be made for common areas, such as hallways, stairwells, or a mailroom.
No Laundry
Per Unit Calculation
No laundry load should be included in the calculations for the individual units' load.*
Laundry Room Load: It is unclear whether a laundry room load should be added to the house load. If no dryer is mentioned, it is likely that no laundry facilities are included in the building. Therefore, no additional load should be allocated for a laundry room. Flag for review