Question: Can a 3-ph MV fused switch feed and protect two transformers? Or, is it required that you need individual primary OCPD for each transformer?If possible, would the primary protection be sized as shown on Table 450.3(A) by adding the 2 transformers rated current?
Can a 3-ph MV Fused Switch Feed and Protect Two Transformers?
Yes, it is possible for a single 3-ph MV fused switch to feed and protect two transformers. However, specific requirements must be met according to NEC regulations.
Requirements
Individual Primary OCPD
Each transformer must have its own individual primary overcurrent protection device (OCPD), such as a fuse or circuit breaker.
Adequate Rating
The fused switch must have a current rating high enough to handle the combined load of both transformers.*
Coordination
The OCPDs for each transformer and the fused switch must be properly coordinated to ensure the proper selectivity and protection.
Protection Sizing
The primary protection of the fused switch should be sized according to Table 450.3(A) of the NEC. However, the individual transformer OCPDs should be sized based on the transformer nameplate ratings.
Coordination
Coordination between the transformer OCPDs and the fused switch should be achieved by properly selecting the time-current characteristics of the devices. The transformer OCPD should trip faster than the fused switch to limit fault current and damage to the transformers.
Conclusion:
While it is possible to use a single 3-ph MV fused switch to feed and protect two transformers, it is essential to meet the NEC requirements for individual primary OCPD, adequate rating, and coordination. The protection should be sized and coordinated properly to ensure selective clearing of faults and protect the transformers and other equipment. Flag for review